Luminance of less than 2,500 cd/m2 between 45 and 90 degrees from nadir
NC-v4 EQc6:Interior lightingposted by Henri Barten on
Hello, i'm new into the LEED requirements.
My customer ask me if we have light fixtures with a luminance of less than 2,500 cd/m2 between 45 and 90 degrees from nadir.
Option 1 Lighting Control - Undeveloped Future Tenant Spaces
NC-v4 EQc6:Interior lightingposted by James Keohane on
I am working on a project that has the majority of individual occupant spaces that will be completely finished with lighting controls meeting the requirements for Option 1. However, we a
Garage Lighting following Strategies A and D
NC-v4 EQc6:Interior lightingposted by Edgar Arevalo on
So i know I left two questions in the past about this topic, and got no response. So hoping third time is the charm since we got comments back from the design credit review.
Reviewer requires cutsheets
NC-v4 EQc6:Interior lightingposted by Edgar Arevalo on
Ok so I get a comment from the LEED reviewer asking for cutsheets of the lighting fixtures to back up the strategies I'm pursuing for the Lighting Quality section of this credit. I need to as
Option 2, A
NC-v4 EQc6:Interior lightingposted by Simon Lai on
In the open office, I'm providing direct/indirect fluorescent up-light, does it meet the exception of the Option 2A?
Theater lighting controls
NC-v4 EQc6:Interior lightingposted by Rafi Karim on
Hi All, we are working on a higher education theater school project where the Theater/Performace spaces do not have lighitng control panel in the same space as the performance because the lights in
INDIA ACP Interior lighting
NC-v4 EQc6:Interior lightingposted by Lalitya Reddy on
Hello LEEDusers,
I am looking for guidance on Interior Lighting credit in LEED v4 and v4.1
How to calculate / count the multi occupant space ???
NC-v4 EQc6:Interior lightingposted by SAMY Chamy on
Hi all,
Translucent fixture for strategy D
NC-v4 EQc6:Interior lightingposted by Omar Elrawy on
IF I have a lighting fixture with direct light, however, the fixture's glass is translucent / white glass. i.e.
Definition of "movable partitions"
NC-v4 EQc6:Interior lightingposted by Stacey Olson on
This appears obvious, but looking for sanity / /confirmation. Can you please confirm "movable partitions" exclude doors?
LEED v4 Interior Lighting Quality Option 2 - Strategy C
NC-v4 EQc6:Interior lightingposted by Ciaran McCabe on
LEED v4 Interior Lighting Quality Option 2 - Strategy C
Art Lab with Machines/ Equipment
NC-v4 EQc6:Interior lightingposted by Johanna Turko on
We have an art lab which has a ton of equipment/machines that students use for metal working/ pottery/ etc.
Manual controls - remote control device
NC-v4 EQc6:Interior lightingposted by A&L SUSTENTABILIDADE on
The EQ credit Interior Lighting – Option 1 - Lighting Control states that “switches or manual controls must be located in the same space as the controlled luminaires.
Are residential building lobbies multi occupant spaces?
NC-v4 EQc6:Interior lightingposted by Gail Vittori on
Are lobbies in residential apartment/condo buildings considered multioccupant spaces and thus subject to comply with lighting controllability requirements if pursuing this credit?
Illuminance Value Calculation
NC-v4 EQc6:Interior lightingposted by on
What program/process is most helpful for caluclating separate illuminance values for ceilings/walls/work surfaces? I have not been able to track down a process that will allow me to do t
Light meter to obtain light reflectance of finishes?
NC-v4 EQc6:Interior lightingposted by Erin Holdenried on
We are having trouble getting light reflectance values from the manufacturer for a number of finishes. Has anybody tried using some sort of light meter to get the value yourself?
Lighting Controls for Natatorium
NC-v4 EQc6:Interior lightingposted by Lyle Axelarris on
It seems to me that it would be inappropriate to have dimmers in a natatorium for safety reasons. Has anyone worked on this credit for a natatorium project?
Thank you
Lighting Levels in Commercial Kitchens
NC-v4 EQc6:Interior lightingposted by Greg Romanczyk on
Is there an exclusion for commercial kitchens needing to meet the EQc6 mutli-occupant lighting levels? We are working on a hotel project, with a restaurant, where the kitchen has switches but
Exterior Lighting Lamp Life
NC-v4 EQc6:Interior lightingposted by Michelle Halle Stern on
This credit is called Interior Lighting. Option 2 Strategy C says "for total connected lighting load", so does exterior lighting need to be included for lamp life?
Option A : Luminance, UGR is working ?
NC-v4 EQc6:Interior lightingposted by Marius Dabonneville on
Hi everyone,
Option 2 Strategy E for an Atrium area - No ceiling areas (Open to roof deck above)
NC-v4 EQc6:Interior lightingposted by John Covello on
Hello.
For Option 2, Strategy E.
Interior Lighting Dimming controls in Multi-use spaces
NC-v4 EQc6:Interior lightingposted by Summer Gorder on
The interior lighting of our projects has 3 zones for dorm rooms, but has dimming with manual on/ automatic off controls. There are also daylight zones.
Lighting coordination with Thermal Comfort
NC-v4 EQc6:Interior lightingposted by Laura strauss on
- Are Janitors Rooms, Storage Rooms, Electrical Rooms, Mechanical Rooms, Elevator Rooms, (not normally occupied rooms) required to conform with controls if listed in the thermal comfort submit
Studio apartment classification
NC-v4 EQc6:Interior lightingposted by Ekaterina Roslavker on
Hi all,
Color muse device
NC-v4 EQc6:Interior lightingposted by Andrew Craven on
We have been pursuing Strategy E, Option 2 in the Interior Lighting credit. We have sealed concrete floors in most of the spaces, which is obviously done in the field and there is no manufact
Light Reflectance for Interior Glazed Walls
NC-v4 EQc6:Interior lightingposted by Gray Bender on
Hi All, We're working on a project that has a number of internal floor-to-ceiling glass walls, some of which are transparent and others are semi-transparent.
Is a Large Multi-Gender Restroom a "Shared Multi-Occupant Space"?
NC-v4 EQc6:Interior lightingposted by Douglas Flandro on
Does a large multi-gender restroom count as a shared multi-occupant space requiring three lighting levels?
EQc6 - Interior Lights (ROS & LRV conflicts)
NC-v4 EQc6:Interior lightingposted by Olawale Taiwo on
There is quite an issue of concern on LRV weighted average calculations on our project per the EQc6 credit, as the project team requires an urgent response to this, please see details bel
Has anybody used microlouvers already?
NC-v4 EQc6:Interior lightingposted by Pierre-Antoine Legrand on
I am trying to figure out how to integrate microlouvers in a double-skin façade.
The architect has decided that only 50% of the louvers would be operated by the user...
Share a task lamp?
NC-v4 EQc6:Interior lightingposted by Kristen Magnuson on
Has anyone ever proposed that 1 task lamp be provided/shared for every 2 employees?
IP-based control system tied to individually controlled fixtures overhead
NC-v4 EQc6:Interior lightingposted by Ciaran McCabe on
Has anoyone gained Option 1 using an IP based control system. If every light fitting can be controlled via an IP based system will this achieve complaince with Option.
Work surfaces in Residential Units?
NC-v4 EQc6:Interior lightingposted by Kristen Magnuson on
Hello,
Option 2 - Strategy F: work surfaces comply but no movable partitions in the project
NC-v4 EQc6:Interior lightingposted by Benjamin Weise on
We are planning to comply with the strategies A, B, C and F. The strategies A, B and C should not pose a problem. However, I am not sure about strategy F:
Default light reflectance values for commodity materials?
NC-v4 EQc6:Interior lightingposted by Joanna Switzer on
Curious if anyone has had success claiming some type of Industry cited / average / worst case LRV for surface finishes such as standard poured in place concrete flooring.
Reflectivity of Sealed concrete
NC-v4 EQc6:Interior lightingposted by Sadie Cline on
The cutsheet of our concrete sealer says 45-65 @60 degrees for the gloss/sheen.
Lighting Controls on restaurants and and gymnasiums
NC-v4 EQc6:Interior lightingposted by Ricardo Sá on
Dear All,
Reflectance
NC-v4 EQc6:Interior lightingposted by Inês Marques on
Hi guys, I'm having troubles getting datasheets with reflectance values for the project I'm working on.
seperate control of presentation walls in small rooms
NC-v4 EQc6:Interior lightingposted by Benjamin Weise on
Hi! There are big medium and small meeting rooms featuring presentation walls. They all have direct lighting from above the tables.
Automatic Daylight dependent Lighting controls and motion detectors
NC-v4 EQc6:Interior lightingposted by Benjamin Weise on
Hello,
Shared Multi-Occupant Spaces within Open Office Layout
NC-v4 EQc6:Interior lightingposted by Sarah Gudeman on
We have a current project with open office layout (individual regularly-occupied spaces) that also includes what I would call huddle areas (shared multi-occupant spaces) distributed around between
Option 2-Strategy A: Spotlights on a light rail
NC-v4 EQc6:Interior lightingposted by Timothy Ian Middleton on
We have an office project pursuing option 2. Our design is mainly downlighting and spotlights on a lighting rail system.
LEED v4 Interior Lighting Quality Option 2, Strategy A
NC-v4 EQc6:Interior lightingposted by Kera Lagios on
Strategy A states: "For all regularly occupied spaces, use light fxtures with a luminance of less than 2,500 cd/m2 between 45 and 90 degrees from nadir." Referring to the luminance tables on cut
Lighting group control for On/Off/Mid Lighting control requirement
NC-v4 EQc6:Interior lightingposted by Thomas Tan on
Dear LEEDusers,
We have a project with a manufacturing space to pursue the Interior lighting control credit. Dimmers for task lights is not acceptable as safety issue.
Following Strategy A but no D for regularly occupied space
NC-v4 EQc6:Interior lightingposted by Edgar Arevalo on
I'm working on a project, where indirect overhead lighting for a regularly occupied space (garbage truck maintenance garage space) would not be feasible due to height restrictions for vehicle
Interior Partitions Option 2: Strategy F without movable partitions?
NC-v4 EQc6:Interior lightingposted by Cindy Quinn on
Has anyone had success earning Interior Lighting Option 2: Strategy F with a project that doesn't have movable partitions? Our project was denied this strategy because we don't have movable p
Fixtures for Option 2 Lighting Quality, Strategy D.
NC-v4 EQc6:Interior lightingposted by Geoffrey Katz on
A recessed LED troffer type fixture may have an indirect light component by way of internal reflectors that reflect upward-directed light within the fixture back down onto the space below.
Strategies E- Casework?
NC-v4 EQc6:Interior lightingposted by LUCY WILLIAMS on
Do you have to consider the color/ light reflectance value of the built-in casework within the occupied spaces, under strategy e? Casework is not technically a wall surface nor is it a work s
IEQ - Interior lighting control (Scene switch)
NC-v4 EQc6:Interior lightingposted by Aravindraj RB on
Hello,
Dimmable Controls
NC-v4 EQc6:Interior lightingposted by Summer Gorder on
Do Dimmable lights suffice for individual workstation lighting control. It seems like theoretically you could provide the three different light level ranges required?
Exam Room Space Definition
NC-v4 EQc6:Interior lightingposted by Summer Gorder on
Our project has a series of exam rooms that we classified as individual, since it is for a particular task with one staff and on additional person.
Entire building vs. parts of the building within scope of work
NC-v4 EQc6:Interior lightingposted by Edgar Arevalo on
In NYC, there is building that the clients are looking to see if it complies with undergoing LEED certification under a Local Law. They pretty much ask for what could be included in the scope
Option 1 - Individual occupant spaces 3 level lighting
NC-v4 EQc6:Interior lightingposted by Mario S. on
For individual occupant spaces, if the overhead lighting is controlled by an on/off switch, and each individual space is provided with an on/off task light (desk lamp or bed side light), does this
Option 2, Strategy E - Exterior glazing possible exclusion from calc?
NC-v4 EQc6:Interior lightingposted by FABIO VIERO on
Since the Option 2, strategies F (partitions), G (floor, wall and ceiling) and H (partition) excluding the fenestrations form calculation, I'm wondering if the exclusion can be apply for the exteri
Lighting control for presentation in meeting room
NC-v4 EQc6:Interior lightingposted by Elyse Dufrene on
LEED requirement says that Lighting for any presentation or projection wall must be separately controlled.
Regularly occupied space that has high bay lighting fixtures but needs to comply with Strategy D
NC-v4 EQc6:Interior lightingposted by Edgar Arevalo on
There is a garage space that acts as an auto service bay (regularly occupied space) but has a high ceiling installed with high bay lighting fixtures. After weighing all other options, no othe
Option 1: Smart-Phone Control
NC-v4 EQc6:Interior lightingposted by RDK E&S on
For option 1, is it acceptable for manual controls to be accomplished via a software interface rather than a physical switch?
Could you confirm the attached cd/m2 results?
NC-v4 EQc6:Interior lightingposted by SSN Energy Model on
Hi,
Greeting!
Option 2 - Strategy H
NC-v4 EQc6:Interior lightingposted by Kaitlin Beeman on
Hello,
I have a few regularly occupied lab spaces with suspended lights at around 12'-8". There is no ceiling in the space and the structure goes up to around 20'-0".
Lighting Quality - Task Lamps
NC-v4 EQc6:Interior lightingposted by Alessia Giannini on
Can project teams be awarded a point under the Lighting Quality, option 1 credit by providing task lamps with dimming capabilities to all of its employees through a request sys
Individual Occupant Space - Task Lighting
NC-v4 EQc6:Interior lightingposted by Daniel Thien on
I've seen several questions on this forum that address task lighting, but I still am a bit confused.
Option 2 Lighting Quality- Part E - LRV
NC-v4 EQc6:Interior lightingposted by Muge Karasahin on
Hello,
We are pursuing strategy E for lighting quality. We received a carpet spec which includes two LRVs:
LRV – L value: 50.4
LRV - Y value: 18.8
Option 1 & 2
NC-v4 EQc6:Interior lightingposted by Christine Chow on
Are existing light fixtures required to be included in the calculations for both options?
Option 1 - "at least three lighting levels"
NC-v4 EQc6:Interior lightingposted by Megan Leslie on
Hi,
Controllability in Gallery/Exhibition spaces
NC-v4 EQc6:Interior lightingposted by Elizabeth Powers on
Does anyone have experience or insight into achieving this credit in gallery or exhibition spaces?
Option 2 Lighting Quality - Part E
NC-v4 EQc6:Interior lightingposted by Jeff Schwane on
We are trying to specify ceilings with at least 85% surface reflectance. However, there are areas with metal ceilings that have perforations for acoustical and fire requirements.
Strategy A - 2500 cd/m2
NC-v4 EQc6:Interior lightingposted by Filipe Boni on
I`m trying to understand the Option 2 -Strategy A and having difficulty of finding this illuminance on brazilian cutsheets. Is this information that I need to look at?
Interior Lighting Quality
NC-v4 EQc6:Interior lightingposted by April Wang on
Regarding EQc6 option 2. I'm working towards satisfying strategies G and H. As part of the requirement, each space is to also meet the corresponding strategies E and F.
EQ credit 6. Interior Lighting Question.
NC-v4 EQc6:Interior lightingposted by Jae Yong Park on
Hi all, I'm currently working on a research center which is located in South Korea. EQ credit 6. Interior Lighting Option 1.
Document Upload
NC-v4 EQc6:Interior lightingposted by Boggarm Setty on
For V4, is there no requirement anymore to upload supporting documents? I don't see any upload buttons on the form itself.
Interior Lighting requirements for plant growth and maintenance
NC-v4 EQc6:Interior lightingposted by Charline SEYTIER on
Hello, We have a project that is considering to install an olive tree in the atrium of the building. To sustain the tree, artificial lighting is required daily, for several hours.
Illuminance vs luminance
NC-v4 EQc6:Interior lightingposted by Dionisio Franca on
Does anyone know why LEED requirements are for illuminance ratios, while WELL and ANSI/IES for Office Light talk about luminance ratios? I guess this is related to how LEED separates reflectance
1 point or 2?
NC-v4 EQc6:Interior lightingposted by Michelle Oishi on
The description of the credit seems to provide two options each worth 1 point but links them with an "OR".
Circadian lighting
NC-v4 EQc6:Interior lightingposted by Brightworks Sustainability on
Does anyone know if there is an alternate strategy for lighting quality that can look at Circadian Rhythm and designing to that? Thanks
Break rooms and/or locker rooms
NC-v4 EQc6:Interior lightingposted by Edgar Arevalo on
I have a Sanitation Maintenance Garage project going for LEED, they have no meeting rooms or classrooms but they do have break rooms and lockers rooms.
" no view down into", how to interpret this?
NC-v4 EQc6:Interior lightingposted by Qiang Zhang on
Interior Lighting question. Option 2. Lighting Quality (1 point) A.
Juvenile Detention Center - Lighting Control
NC-v4 EQc6:Interior lightingposted by Michelle Bombeck on
Hello all - We are working on a juvenile detention center and are trying to find a way to comply with EQc6.2.
Option 2 Documentation
NC-v4 EQc6:Interior lightingposted by Charalampos Giannikopoulos on
When it comes to option 2 it is request to describe the method for determining reflectance values. Would a prescriptive descriptive apporach be accepted i.e. based on colour selection?
Lighting control in office space
NC-v4 EQc6:Interior lightingposted by Jeroen Sap on
I am working on an office building that has overhead lighting that is controlled based on occupancy sensors. The fixtures are grouped per 3,6 meters and there is no manual override.