LEED requirement says that Lighting for any presentation or projection wall must be separately controlled. Our project have small multiple meeting room where hanging on the wall TVs are used for presentation. As meeting room are small (4-6 person capacity), the engineer don't plan to design separate control for presentation wall. Besides, as presentation tool is a TV, lighting adjustment can be made on the TV to optimise visibility of the screen while occupants have enough light to take notes. Is it essential to have Lighting control for presentation wall? Tks
You rely on LEEDuser. Can we rely on you?
LEEDuser is supported by our premium members, not by advertisers.
Go premium for $15.95 »
Joyce Kelly
Architect - Cx Provider - Building Performance SpecialistGLHN Architects & Engineers
27 thumbs up
August 31, 2018 - 12:30 pm
If the lighting adjacent to presentation / projection / television wall casts light on that wall, it should be separately controlled and ideally, dimmable for optimum lighting conditions in the space. If it's a focused beam of light that doesn't illuminate the wall, you could make a case for not controlling it separately.