EZEBOM-2009 IEQp1: Minimum indoor air quality performanceposted by Cheryl Burkinshaw on Mar 4, 2014, 5:18 pm
I am working on a small project with a design team that is fairly new to LEED. We are working on IEQ P1 and would like to find some direction on selecting the correct EZ value to be used in... Last reply: Noriko Nagazumi, Mar 17, 2014, 3:09 am |
|
IEQp1 Design Supply Air QuestionEBOM-2009 IEQp1: Minimum indoor air quality performanceposted by AshLee Eustace on Sep 18, 2012, 3:05 pm
Hi, For the Design total supply to zone (Vdzd) and Design total supply airflow (Vpsd), should those numbers reflect the design flow at the condition analyzed? For example, if I am... Last reply: Jerry Scott, Mar 11, 2014, 7:42 pm |
|
One outside air intake for multiple AHUsEBOM-2009 IEQp1: Minimum indoor air quality performanceposted by Ilona Johnson, PE, CEM, LEED AP on Mar 6, 2014, 10:14 am
Has anyone had experience documenting IEQp1 in the following situation?: Last reply: Dave Hubka, Mar 6, 2014, 10:28 am |
|
VAV minimum for DsEBOM-2009 IEQp1: Minimum indoor air quality performanceposted by George Kotsis on Aug 21, 2013, 4:58 pm
Hello all, Last reply: Julia Weatherby, Feb 13, 2014, 1:11 pm |
|
Using the calculator (continued)EBOM-2009 IEQp1: Minimum indoor air quality performanceposted by Christina Reeves on Feb 13, 2014, 8:41 am
Hello again, Last reply: Julia Weatherby, Feb 13, 2014, 1:02 pm |
|
Using the 62MZ calculatorEBOM-2009 IEQp1: Minimum indoor air quality performanceposted by Christina Reeves on Feb 10, 2014, 11:15 am
Hello, I have two questions from our ME about using the spreadsheet calculator: Last reply: Christina Reeves, Feb 10, 2014, 12:45 pm |
|
Testing and Balancing vs. BAS MeasurementEBOM-2009 IEQp1: Minimum indoor air quality performanceposted by Marc Mondor on Jan 4, 2011, 5:20 pm
Dear All, We've got a BAS in place that measures outside air flow for all major HVAC systems, but have not had our facility tested and balanced within the last two years. Does... Last reply: Julia Weatherby, Jan 24, 2014, 12:57 pm |
|
Subtracting built-in furniture/casework from square footageEBOM-2009 IEQp1: Minimum indoor air quality performanceposted by American University on Jan 23, 2014, 3:10 pm
We've had a designer tell us that built-in furniture and case work (like a fan-coil unit... Last reply: Julia Weatherby, Jan 23, 2014, 4:28 pm |
|
Exhaust Systems ReportEBOM-2009 IEQp1: Minimum indoor air quality performanceposted by Richard Navarro on Feb 9, 2011, 3:06 pm
Hi all, We received our comments back from the reviewers and it appears we are missing our exhaust systems report. It was found that the contractor who did our air balance reports did not... Last reply: Nelina Loiselle, Jan 21, 2014, 2:55 pm |
|
Type and sub-type area matrix IEQ EBOMEBOM-2009 IEQp1: Minimum indoor air quality performanceposted by Hector Miranda on Nov 6, 2013, 10:20 pm
I have a question if a have in an... Last reply: Tristan Roberts, Dec 20, 2013, 12:55 pm |