10% exemptionEBOM-2009 IEQp1: Minimum indoor air quality performanceposted by Gustavo De las Heras Izquierdo on May 17, 2016, 6:41 pm
Is it allowed to exclude up to 10% of spaces from this prerequisite? Our project is a 20-story building that complies with the ventilation rates but there is an office in the core that... Last reply: Michael Smithing, Jan 16, 2017, 7:27 pm |
|
EBOM IEQp1-A1 Statement "Would need over 100% OA Intake"EBOM-2009 IEQp1: Minimum indoor air quality performanceposted by James Doyle on Jul 31, 2014, 8:50 am
Our EBOM 2009... Last reply: Gustavo De las Heras Izquierdo, Dec 15, 2016, 5:53 pm |
|
CO2 measurementsEBOM-2009 IEQp1: Minimum indoor air quality performanceposted by Gustavo De las Heras Izquierdo on Oct 26, 2016, 11:57 am
Hallo, In our project there are AHUs providing a mix of outdoor and return air. Due to the machine room layout, it is very difficult to measure outdoor airflow (cfm). There is a... Last reply: Gustavo De las Heras Izquierdo, Oct 27, 2016, 2:27 pm |
|
Exhaust system testsEBOM-2009 IEQp1: Minimum indoor air quality performanceposted by Agnieszka Rylska on Oct 28, 2015, 5:43 am
I have two questions regarding exhaust system tests: Last reply: Dave Hubka, May 24, 2016, 4:30 pm |
|
Parking exhaustEBOM-2009 IEQp1: Minimum indoor air quality performanceposted by Emmanuel Pauwels on Apr 25, 2016, 8:04 am
Do parking spaces or restrooms need to comply with Ashare exhaust rates of table 'TABLE 6-4 Minimum Exhaust Rates'? Last reply: Dave Hubka, Apr 26, 2016, 9:02 am |
|
Public Corridors Lack VentilationEBOM-2009 IEQp1: Minimum indoor air quality performanceposted by Ali Stricks on Apr 8, 2014, 5:54 pm
I’m dealing with a building that generally meets ASHRAE 62.1, however several public corridors are unconditioned and unventilated. The corridors do not have the minimum 0.06 cm/sf required per... Last reply: Ben Stanley, Mar 3, 2016, 5:43 pm |
|
Physical constraintsEBOM-2009 IEQp1: Minimum indoor air quality performanceposted by Gustavo De las Heras Izquierdo on Feb 21, 2016, 9:19 pm
Hallo, I am wondering what is the Reference Guide referring to when it says "physical constraints of the existing ventilation system". For instance, should I consider a "physical... Last reply: Ben Stanley, Mar 3, 2016, 5:36 pm |
|
Case 1- Grouping the space typesEBOM-2009 IEQp1: Minimum indoor air quality performanceposted by satheesh M on Dec 16, 2015, 6:19 am
Hi, we are working for the project with multiple tenants. we could not collect all the floors HVAC layouts. but we have the... Last reply: Hugo Teixeira, Feb 16, 2016, 1:34 pm |
|
Airflow testing serviceEBOM-2009 IEQp1: Minimum indoor air quality performanceposted by Saul Pichardo, AIA on Jan 26, 2016, 5:30 pm
Hi All, We are looking for a company in the San Francisco Bay Area who can conduct the airflow tests in our commercial building (in the office area). We are working on a LEED O&M... |
|
Option B CalculatorEBOM-2009 IEQp1: Minimum indoor air quality performanceposted by Haley Duncan on Sep 16, 2015, 2:56 pm
Where can I find the Option B Calculator that is used to calculate compliance with 10 CFM per person for... Last reply: Trista Brown, Jan 25, 2016, 5:59 pm |