I'm curious if anybody out there has developed specification language requiring a certain level of airtightness (as assessed via one or a series of blower door tests) for a commercial project when it is not going for a Passive House certification and a blower door test is not required by code--basically, something in the contract documents to hold the contractor accountable for doing a good job on air sealing without an external enforcer/standard. Is that just a pipe dream, or has anyone successfully implemented this without the contractor balking?
Thanks for any advice,
Misha
The DoD set their goal at 0.25 cfm/sf @ 75Pa, based on some studies of what was acheivable on retrofits of army barracks done back in 2013.
We have incoroporated this USACE target into our spec for larger projects for the last decade.
Contractors often side-step the 'execution' requirement in our spec that the envelope be tested after the envelope is complete but before the installation of interior gypsum wall board that would impede access to likely leaking points for easy fixes. They also complain about existing buildngs being "inherently leaky" but we tell them to run the test, look for and fix what leaks they can, and we will be merciful. When we have done before-and-after renovation testing, we often find 1.5 cfm/sf is common for old existing buildings and 0.5 cfm/sf is routinely achieved even with our least attentive contractors.