Log in
Forum » NC-2009 EAp2
Topic

Lighting Power Density Using The Building Area Method

NC-2009 EAp2: Minimum Energy Performance
posted by Curtis Clark on Jun 24, 2014, 5:38 pm

How do you apply Building Area Method (ASHRAE Table 9.5.1) to a higher education building that has five building area types?
1. School/University
2. Dining: Cafeteria/Fast Food
...

Last reply: Marcus Sheffer, Jun 25, 2014, 10:22 am

HVAC Climate Zone 1

NC-2009 EAp2: Minimum Energy Performance
posted by John Covello on Jun 24, 2014, 6:24 am

Hello,

We are working on an office space in climate zone 1. ASHRAE 90.1 does not require heating for these zones. Is some form of cooling such as air conditioning required?

John...

Last reply: Marcus Sheffer, Jun 24, 2014, 9:08 am

Central Chilled Water Plant

NC-2009 EAp2: Minimum Energy Performance
posted by Marcus Sheffer on Mar 31, 2011, 12:31 pm

We are investigating how a building which houses a central chilled water plant for a campus can meet the prerequisite. This building houses the chillers and cooling towers plus some electrical...

Last reply: Jon Clifford, Jun 23, 2014, 5:21 pm

Parallel PIU fan energy

NC-2009 EAp2: Minimum Energy Performance
posted by Magda Aghababyan on Jun 20, 2014, 7:00 am

My baseline is under system 6 in which the parallel PIU fans has to be introduced for each zones. I calculated the main supply fan power as per section G3.1.2.9 and inserted to eQuest under...

Last reply: Marcus Sheffer, Jun 20, 2014, 10:39 am

Ventilation- Proposed and Baseline per ASHRAE 62.1-2007?

NC-2009 EAp2: Minimum Energy Performance
posted by Todd Tewksbury on Jun 13, 2014, 9:13 am

Hi!

I am conducting a LEED v2009 EAp2/c1 energy model for a nonresidential building that is more than 5 floors. The proposed system is a water source heat pump system (WSHP) with natural...

Last reply: Marcus Sheffer, Jun 17, 2014, 9:46 am

Roof insulation & suspended ceiling

NC-2009 EAp2: Minimum Energy Performance
posted by Charline SEYTIER on Jun 17, 2014, 1:02 am

Hi everyone,
We are working on a major renovation project where the owner wants to install roof insulation above the suspended ceiling. ASHRAE 90.1 mandatory provisions exclude that option...

Last reply: Marcus Sheffer, Jun 17, 2014, 9:38 am

Baseline HVAC System Types- Number of floors

NC-2009 EAp2: Minimum Energy Performance
posted by CT G on Jun 12, 2014, 1:13 pm

Dear all,

In the selection of the HVAC system for baseline according to Table G3.1.1A should the unconditioned underground parking pavements be considered in the number of floors of the...

Last reply: CT G, Jun 12, 2014, 1:45 pm

ASHRAE Mandatory Provisions & Existing skylights not replaced

NC-2009 EAp2: Minimum Energy Performance
posted by Charline SEYTIER on Jun 11, 2014, 9:56 am

Hi everyone,

I'm currently working on a major renovation project.
The owner is renovating & insulating the entire building but doesn't wish to replace the existing old single...

Last reply: Marcus Sheffer, Jun 12, 2014, 8:59 am

Baseline for Ventilation Fan unconditioned space?

NC-2009 EAp2: Minimum Energy Performance
posted by Zonda E. Team on Jun 11, 2014, 1:17 am

What is the baseline for a ventilation fan providing outdoor air to an unconditioned space? I understand "G3.1.2.9 System Fan Power", only applies to fans within a system, meaning fan that are...

Last reply: Marcus Sheffer, Jun 11, 2014, 9:01 am

metal wall louvers

NC-2009 EAp2: Minimum Energy Performance
posted by Francesco Passerini on Jun 9, 2014, 4:17 am

In the building that I’m modeling there are metal wall louvers. Some of them are connected to ductwork (for ventilation), some of them ventilate directly technical rooms. From the point of view...

Last reply: Zonda E. Team, Jun 11, 2014, 8:53 am