Forum quick links
parking garage
EBOM-2009 IEQc1.4:IAQ Best Management Practices—Reduce Particulates in Air Distributionposted by Alison Rizzo on
Does there have to be a MERV13 filter on makeup air units supplying outdoor air for parkade exhaust?
Occupied only OR All outdoor air ventilated spaces
EBOM-2009 IEQc1.4:IAQ Best Management Practices—Reduce Particulates in Air Distributionposted by Petr Vogel on
Dear all, is this credit related to all: • regularly occupied OR • occupied OR • all outdoor air ventilated spaces? When following the intent of the credit only occupied spaces would make sense t
Evaporative cooler
EBOM-2009 IEQc1.4:IAQ Best Management Practices—Reduce Particulates in Air Distributionposted by Lourdes Salinas on
As we all know LEED requires MERV 13 filters for all outdoor air intakes. We are currently working on a manufacturing plant in a desert region that mostly operates with evaporative coolers.
electronic air filters
EBOM-2009 IEQc1.4:IAQ Best Management Practices—Reduce Particulates in Air Distributionposted by Iris Amdur on
Have any projects used electronic air filters (in conjunction with MERV 8 filters) as an alternative compliance path for this credit?
Indoor AHUs and MERV 13 filters
EBOM-2009 IEQc1.4:IAQ Best Management Practices—Reduce Particulates in Air Distributionposted by Wendy Gibson on
The first paragragh in your "birds eye view" states that "As of November 2010, a USGBC addendum removed a requirement for return air circulation to also have MERV 13 filtration." Below is the Novem
Non-compliant pre-filters
EBOM-2009 IEQc1.4:IAQ Best Management Practices—Reduce Particulates in Air Distributionposted by Eddie Cuevas on
I am working on a project with several large outdoor air handlers. Each air handler has a system of MERV 8 pre-filters followed by MERV 13 main filters.
Filter Performance
EBOM-2009 IEQc1.4:IAQ Best Management Practices—Reduce Particulates in Air Distributionposted by Alexa Stone on
Has anyone ever had an issue with MERV 13 filters not maintaining original quality and performance levels? Also, I cant find if this credit requires active monitoring of any sort that would capture
MERV 13
EBOM-2009 IEQc1.4:IAQ Best Management Practices—Reduce Particulates in Air Distributionposted by susan eguia on
Our building has existing MERV 8. The existing HVAC does not have the capability to to take MERV-13 filters. Can we get this credit if we have phase-out plan or need to replace all at once?