EBOM-2009 IEQc1.4:Indoor air quality best management practices - reduce particulates in air distribution

Non-compliant pre-filters

I am working on a project with several large outdoor air handlers. Each air handler has a system of MERV 8 pre-filters followed by MERV 13 main filters. Would this credit be achievable considering the current set-up? Thank you.

1

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Wed, 07/17/2013 - 18:22

Eddie, according to the credit language (see above), you simply have to use MERV 13 filters prior to air being introduced to occupied spaces. So I don't see any problem with your situation.

Thu, 07/18/2013 - 14:20

Eddie, Tristan is correct. This complies and is actually a very typical situation. The pre-filters are there to lengthen the life of the more expensive MERV 13 filters.