Post a question or comment
Credit Filters
Minimum IAQ Performance
Filter by location
Forum
Topic
Replies
Recent

Minimum Indoor Air Quality Performance Calculation

NC-2009 IEQp1:Minimum IAQ Performance
posted by  Amal Venugopal  on 

My Project is Having one FAHU on roof which is supplying treated Fresh air to all AHU"s, which further supplying the mixture of outdoor air and Recirculated air to various zone via VAV (no reheatin

7
Default Avatar
Senior Manager - Sustainable Services
Surmount
LEEDuser Basic Member
29 thumbs up
Sat Apr 29, 2023, 8:16 pm

Basement lobbies

NC-2009 IEQp1:Minimum IAQ Performance
posted by  Marni Punt  on 

We have a project with 3 lobbies located in basement parking.

4
Default Avatar
Senior Manager - Sustainable Services
Surmount
LEEDuser Basic Member
29 thumbs up
Sat Apr 29, 2023, 8:07 pm

Data center outside air requirement

NC-2009 IEQp1:Minimum IAQ Performance
posted by  HOUCINE TLEMSANI  on 

I am working on a data center and not sure about ASHRAE 62.1-2007 outside air requirement.

7
Mon Sep 26, 2022, 5:54 am

ASHRAE 62.1 2013 for NC-2009 IEQp1 - Minimum IAQ Performance

NC-2009 IEQp1:Minimum IAQ Performance
posted by  Ganesh Dhanakotti  on 

Hi,

Our project consists of office building and workshop which is going for  LEED v3 2009.

2
Thu Dec 17, 2020, 3:37 pm

Adding Kitchens in the Minimum IAQ Performance Calculator

NC-2009 IEQp1:Minimum IAQ Performance
posted by  Edgar Arevalo  on 

There is no clear selection for kitchens in the occupancy category of the calculator, and yet when I took a look at the IEQ matrix it shows Kitchen spaces are to be included for IEQp1.  N

3
Energy Engineer
ads ENGINEERS, DPC
LEEDuser Basic Member
21 thumbs up
Sat Oct 3, 2020, 7:56 pm

Art-center

NC-2009 IEQp1:Minimum IAQ Performance
posted by  Suren Melkumyan  on 

Can anyone tell us about the requirements of table 6-1 and 6-4 ASHRAE regarding air exchange? Judging from what I understand Russia has more stringent regulatory requirements

0

Zones served by mutli-zone unit but is exhausted separately

NC-2009 IEQp1:Minimum IAQ Performance
posted by  Edgar Arevalo  on 

This may be nothing, but should I still count for zones that are served by a multizone unit but the ventilated air is not recirculated back to the unit?  The air is pretty much exhausted throu

5
Energy Engineer
ads ENGINEERS, DPC
LEEDuser Basic Member
21 thumbs up
Tue Nov 19, 2019, 3:03 pm

IEQp1 for Residencial Buildings

NC-2009 IEQp1:Minimum IAQ Performance
posted by  Diego Escalona  on 

Hello, We have a 20-storey residential building, which will be naturally ventilated, so to meet IEQp1, naturally ventilated spaces shall be permanently open to the outside at a distance of 8 meter

2
Fri Aug 23, 2019, 4:02 pm

Entrance vestibules and stairs

NC-2009 IEQp1:Minimum IAQ Performance
posted by  Dionisio Franca  on 

Do vestibules at the entrance of buildings require mechanical ventilation?

5
Mon Feb 4, 2019, 11:31 pm

Ventilation rates in garages

NC-2009 IEQp1:Minimum IAQ Performance
posted by  Maria Porter  on 

My projects can follow the Ventilation Rate Procedure in ASHRAE 62.1-2007, sections 4 through 7 without bigegr problems.

3
Sustainability specialist
Skanska Sweden
LEEDuser Basic Member
205 thumbs up
Fri Feb 1, 2019, 1:43 pm