Forum discussion

NC-2009 IEQp1:Minimum indoor air quality performance

IEQp1 for Residencial Buildings

Hello, We have a 20-storey residential building, which will be naturally ventilated, so to meet IEQp1, naturally ventilated spaces shall be permanently open to the outside at a distance of 8 meters (25ft) of a wall or opening useful in roofs, the opening area must be at least 4% of the net occupiable floor area. The question is: Does this percentage should be constantly open to ensure ventilation, or is it sufficient that this percentage is only operable?

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Tue, 10/23/2012 - 19:59

Hi Diego Section 5.1.1 of ASHRAE 62.12007, speaks about the space being "permanently open to and within 8 m (25 ft) of operable wall or roof openings to the outdoors, the openable area of which is a minimum of 4% of the net occupiable floor area." Based on this, it is enough that the openings to the outdooors are operable and don't need to be constantly open. I hope this helps

Fri, 08/23/2019 - 16:02

Hi, Is this also applicable to residential v4 projects? 

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.