I am working on a data center and not sure about ASHRAE 62.1-2007 outside air requirement. Table 6.1 list 2 types: Computer lab at 10 CFM/ person and 0.12 CFM/Sqf and Computer no printing at 0.06 CFM/Sqf only.
it is not really clear where the data center will fall.
Any help will be appreciated.
thanks
You rely on LEEDuser. Can we rely on you?
LEEDuser is supported by our premium members, not by advertisers.
Go premium for
Andrew Mitchell, P.E.
PrincipalMitchell Gulledge Engineering, Inc.
LEEDuser Expert
126 thumbs up
April 11, 2014 - 8:10 am
When you say data center it is unclear what type of room you are referring to. The first thing that comes to my mind is a server room. For the most part, these are unoccupied spaces and do not require ventilation; much like an electrical room. You need to pay special attention to whether or not you have a UPS system in the same space and also if you determine that there are any local contaminants that will need to be exhausted from the room.
Kimberly Hosken
LEED Fellowsubcontractor
8 thumbs up
April 14, 2014 - 11:26 am
I am working on a Tier III data center with the same question. Our server room will be occupied for a few years with between 1 to 5 FTE's working on daily basis. FTE's will taper off over time as server space is leased. I am therefore wondering what is correct CFM? Our UPS is outside the space.
HOUCINE TLEMSANI
Mechanical DesignerMEP Engineering Solutions, Inc
14 thumbs up
April 14, 2014 - 12:43 pm
yes its a server room, UPS is located in a separate room with its own system.
the room will be unoccupied just for maintenance. we have decided to bring outside air for pressurization. that will be close to the 0.06 CFM / Sqf.
Thanks.
Andrew Mitchell, P.E.
PrincipalMitchell Gulledge Engineering, Inc.
LEEDuser Expert
126 thumbs up
April 14, 2014 - 4:12 pm
Kimberly, in your case I would use the same rates as a computer room without printing.
Houcine, you will be fine with a small amount of pressurization air. You are simply doing more than what is required.
jamsheer ali
1 thumbs up
July 24, 2022 - 8:54 am
kindly advice me about OA requirement for Battery room as per ashrae/ any standard ( in % of supply air)
jamsheer ali
1 thumbs up
July 24, 2022 - 8:59 am
i want to design cooling load calculation in HAP software for a refinery building. please advice me about fresh air requirement.
requirement is 1 package unit and 1 fresh air unit.
Dionisio Franca
DirectorWoonerf Inc.
30 thumbs up
September 26, 2022 - 1:54 am
Another way to formulate the questions here would be: Is the data hall or the UPS room an occupiable space or not?
The definition for occupiable space is:
occupiable space: an enclosed space intended for human
activities, excluding those spaces that are intended primarily
for other purposes, such as storage rooms and equipment
rooms, and that are only occupied occasionally and for short
periods of time.
It is a judgement call, and therefore risky for the consultant to assume such spaces are not occupiable because the understanding of the reviewer is not known.
If you want to get an official response from USGBC, you need to contact them and hope the response comes before the design drawings need to be completed.