HAP boiler input data
NC-2009 EAp2:Minimum Energy Performanceposted by PAWAN DAHIWAL on
is estimated max load reported in HAP boiler input data for baseline case same to that of total heating capacity reported in Table 1.4 HVAC (water side) for baseline???. In one of the project Est
Heat recovery and dehumidification
NC-2009 EAp2:Minimum Energy Performanceposted by Francesco Passerini on
In a swimming pool removing latent heat is necessary all the year round. For the baseline model, if I model the heat recovery according to G3.1.2.10 Exhaust Air Energy Recovery (50% both sensible a
Diesel generator for peak shaving
NC-2009 EAp2:Minimum Energy Performanceposted by Luana Bertoletti on
Hi, I'm involved in a project which will regularly use a diesel generator for peak shaving. May I use this strategy ir order to verify compliance with EA.p2 and take credit in EA.C1?
Task light process load or lighting load?
NC-2009 EAp2:Minimum Energy Performanceposted by Haojie Wang on
I saw some people say task light is process load but sometimes it can be count into lighting power. I wonder is there a good way to treat task light?
LPD part of mandatory provisions?
NC-2009 EAp2:Minimum Energy Performanceposted by Tatjana Ernst on
Hi everyone, i am wondering if the interior lighting power is also restricted by LEED. Do we have to show compliance with the table 9.5.1 or 9.6.1 in ASHRAE?
Modeling KFC
NC-2009 EAp2:Minimum Energy Performanceposted by Vassil Vassilev on
Hi Marcus and colleagues, The project we have to model is a KFC fast food complex, having GFA of 300 m2 single floor. In accordance to App.
Target Finder: Design vs Target
NC-2009 EAp2:Minimum Energy Performanceposted by Rock Ridolfi on
All, new to energy modeling and reviewing the EAp2 online template trying to figure out the required inputs and reports for the Target Finder section, Design vs Target.
Fan power in conditioned space
NC-2009 EAp2:Minimum Energy Performanceposted by Panupant Phapant on
Hello, My production line space in our project have an supply fan, exhaust fan and make-up fan to supply OA in conditioned space.
Determining R-values for LEED wall assembly
NC-2009 EAp2:Minimum Energy Performanceposted by Todd Bundren on
Is there a standard way the USGBC wants the R-value of a wall assembly to be calculated taking into account the framing factor or thermal bridging that occurs with metal studs?
Baseline heating set-point when no heating system exists
NC-2009 EAp2:Minimum Energy Performanceposted by Ricardo Sá on
According to ASHRAE 90.1 (2007) Table G3.1 - 10 c, "where no heating systems exist, HVAC system shall be assumed to be electric".