FAQs about EAp2 :

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

View answers »

Forum discussion

NC-2009 EAp2:Minimum energy performance

School Building

Hi, We are doing the Energy Model for SCHOOL Building. The client has proposed Air cooled chiller. Class rooms are served by individual FCU, Meeting rooms are served by split units, and Auditorium, Lobby spaces are served by AHU. Separate FAHU will be used to provide fresh air to all those areas. In Base Case, we have considered packaged VAV and Fan power has considered as as 0.0013 bhp/cfm (Total Fan Power = 17 kW). In Proposed Case - We have considered FCU Fan power as 0.55 W/LPS (Total Fan Power = 7 kW)., AHU Fan power as 1.2 W/LPS (Total Fan Power = 5 kW).. FAHU Fan power as 1.6 W/LPS (Total Fan Power = 8 kW) Total Fan power Basecase= 17 KW Total Fan power Proposed case= 20 KW 1) In our software, not possible to model FAHU, so we have distributed the total fan power (of FAHU) 8Kw to FCU’s and AHU’s. This total KW has converted into BHP and this BHP value has used to calculate BHP/CFM. Finally BHP/CFM for FCU,AHU has been entered in the software. Is this correct or Whether we need to remove FAHU from energy model 2) Whether the BC Fan power 0.0013 bhp/cfm (from Table G3.1.2.9) should be considered only for supply air 3) Whether we can consider FAHU in base case also? (Because while considering FAHU only in PC, we are getting negative savings) 4) For what kind of fan system (like FCU,AHU,FAHU, Kitchen Exhaust and Toilet Exhaust) , table G3.1.2.9 will be used and is there any spread sheet? Thanks for your suggestions, Regards, Sam

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Wed, 05/25/2016 - 13:43

1. The Proposed must be modeled as designed so the FAHU must be included. The method you propose to model the FAHU appears correct. 2. The Baseline fan power includes all of the fans (supply, return, relief and exhaust) but the allowance is calculated using only the supply airflow. You can distribute the baseline fan power anyway you like. We usually do it in proportional to the proposed systems. 3. There should be no FAHU in the baseline. 4. There is a spreadsheet in the Documentation Toolkit above that can be used for the baseline fan power calculations. G3.1.2.9 is only applied to the baseline fans that are related to the space conditioning equipment.

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.