Post a question or comment
Filter by location
Forum
Topic
Replies
Recent

Data Center CxA

NC-v4 EAp1:Fundamental commissioning and verification
posted by  Peter Dishno  on 

The LEED V4 book has the comment: "DATA CENTERS ONLY For small projects with computer room peak cooling loads less than 2,000,000 Btu/h (600 kW) or a total computer room peak cooling load less tha

4
Default Avatar
Commissioning Engineer
LEEDuser Basic Member
15 thumbs up
Sun Feb 19, 2017, 10:24 pm

Maximum threshold for General VOC emissions compliance?

NC-v4 EQc2:Low emitting materials
posted by  Joanna Switzer  on 

Hi, I am not finding any info to suggest a maximum VOC limit allowable under the General Emissions. Does "5.0 mg/m3 or more" really include everything greater than 5.0mg?

5
Independent consultant on VOC issues
formerly with Eurofins Product Testing A/S
LEEDuser Basic Member
246 thumbs up
Sun Feb 19, 2017, 5:53 am

Clear definition for interior/exterior needed

NC-v4 EQc2:Low emitting materials
posted by  Björn Schön  on 

The Definition of interior/exterior in the LOW-EMITTING MATERIALS credit is a bit confusing for me.

3
Independent consultant on VOC issues
formerly with Eurofins Product Testing A/S
LEEDuser Basic Member
246 thumbs up
Sun Feb 19, 2017, 5:49 am

Demonstration that plants are native or adapted

CS-2009 SSc5.1:Site Development—Protect or Restore Habitat
posted by  David Lazaro  on 

Hello, We are encountering some problems as to deciding which vegetation species can be counted as adapted. In a Mediterranean country, there are many plants that grow well in our city.

2
Founder & Community Director
Metricorps
LEEDuser Expert
7781 thumbs up
Fri Feb 17, 2017, 5:54 pm

No FTE

NC-v4 MPR3:Must comply with project size requirements
posted by  Claire DeCamp  on 

We've got a building with no FTE - it houses mostly lab equipment that is managed by a researcher and then left alone. There are no restrooms, offices, etc.

5
Default Avatar
LEED AP BD+C
MZ and Partners
LEEDuser Basic Member
0 thumbs up
Thu Feb 16, 2017, 11:38 pm

VOC information

CS-2009 IEQc4.1:Low-Emitting Materials—Adhesives and Sealants
posted by  Lilian Seow  on 

Is it necessary for manufacturer to indicate 'less water" for the VOC limit?

4
LEED-AP BD+C
GREENSQUARE
LEEDuser Expert
261 thumbs up
Fri Feb 17, 2017, 3:09 pm

Spaces controlled by both daylight and occupancy sensors

CI-2009 EAc1.2:Optimize Energy Performance—Lighting Controls
posted by  Edgar Arevalo  on 

I have a project that has spaces which are controlled by both an occupancy sensor and a separate daylight sensor that is installed within 15 feet of the windows.

2
Director - Green Building Advisory
Colliers International Ltd.
LEEDuser Basic Member
201 thumbs up
Fri Feb 17, 2017, 2:54 pm

Emission tests for 2-component epoxy flooring systems

NC-v4 EQc2:Low emitting materials
posted by  Björn Schön  on 

According to the LEED v.4 credits, it is possible to use different emission tests outside the US to comply with the requirements. AgBB and DiBt testing method (2010) are mentioned there. But accor

3
Independent consultant on VOC issues
formerly with Eurofins Product Testing A/S
LEEDuser Basic Member
246 thumbs up
Fri Feb 17, 2017, 6:40 am

Definition of "Sourced"?

NC-v4 MRc2:Building product disclosure and optimization - environmental product declarations
posted by  Douglas Flandro  on 

The credit language says,"For credit achievement calculation, products sourced (extracted, manufactured, purchased) within 100 miles (160 km) of the project site are valued at 200% of their base co

2
Editorial Director
BuildingGreen, Inc.
LEEDuser Expert
159 thumbs up
Thu Feb 16, 2017, 7:30 pm

EAP2 Minimum Energy Performance -- How to classify building

EBOM-2009 EAp2:Minimum Energy Efficiency Performance
posted by  cathy keagle  on 

We have a client that would like to attempt to certify one building that is part of a college campus. This building is primarily instructional classrooms, some office space, and an auditorium.

6
Senior Sustainability Manager
WSP - Built Ecology
LEEDuser Expert
188 thumbs up
Thu Feb 16, 2017, 5:52 pm