Existing Central Plant and New building

NC-2009 EAp2:Minimum energy performance
posted by  Mital Patel  on 

We have a new building that is served by the existing central plant.

2
Default Avatar
Energy Modeler
KJWW Engineering
LEEDuser Basic Member
3 thumbs up
Fri Jul 24, 2015, 3:15 pm

AC Split units as misc. load

NC-2009 EAp2:Minimum energy performance
posted by  Vassil Vassilev  on 

Hi Markus, There is an issue with the project we're modelling, where your opinin would be highle appreciated. The main HVAC system of our project (small retail building) consists of rooftop units a

4
LEED Fellow
7group / Energy Opportunities
LEEDuser Expert
4461 thumbs up
Tue Jul 14, 2015, 3:33 pm

Energy Modeling- VisDOE Query

NC-2009 EAp2:Minimum energy performance
posted by  Sasha Peters  on 

Kindly request for any advise on VisDOE limitation concerning large buildings. I'm working on a mixed use project that is first of all odd shaped with a gross area 3,969,058 sqft.

3
Tue Jul 14, 2015, 12:44 pm

Domestic Water Heating

NC-2009 EAp2:Minimum energy performance
posted by  David Mirabile  on 

I am modeling a school in which we are using several water-to-water geothermal heat pumps for our domestic water heating.

18
LEED Fellow
7group / Energy Opportunities
LEEDuser Expert
4461 thumbs up
Fri Jul 10, 2015, 8:59 am

G3.1.1 Exception a

NC-2009 EAp2:Minimum energy performance
posted by  Haojie Wang  on 

I have a convention center project where it has a exhibit hall with high process load. It is larger than 20k ft2.

2
LEED Fellow
7group / Energy Opportunities
LEEDuser Expert
4461 thumbs up
Wed Jul 8, 2015, 4:33 pm

Energy recovery from a nearby data center?

NC-2009 EAp2:Minimum energy performance
posted by  Haojie Wang  on 

We have a project that is planning to use energy recovery from a nearby data center. The rest of the heat and cooling are provided by a district plant.

4
LEED Fellow
7group / Energy Opportunities
LEEDuser Expert
4461 thumbs up
Mon Jul 6, 2015, 4:30 pm

Fume hood exhaust fan process load?

NC-2009 EAp2:Minimum energy performance
posted by  Haojie Wang  on 

I think fume hood exhaust are unregulated in 90.1 2007 thus should be process load. But just want to confirm. I do see EPAct 2005 says fume hood should not be treated as process load...

3
Default Avatar
Energy Modeler
KJWW Engineering
LEEDuser Basic Member
3 thumbs up
Mon Jul 6, 2015, 4:07 pm

Basline system for 5 floors + small below grade conditioned spac

NC-2009 EAp2:Minimum energy performance
posted by  Zonda E. Team  on 

What is in your opinion the baseline for the following building: Floor area:12,000 sqm (130,000 sqft) Floors: 5 above grade, mostly conditioned.

2
LEED Fellow
7group / Energy Opportunities
LEEDuser Expert
4461 thumbs up
Sat Jul 4, 2015, 7:31 pm

small DES

NC-2009 EAp2:Minimum energy performance
posted by  Francesco Passerini  on 

For a preliminary review I modeled a building that is heated and cooled by four geothermal heat pumps that are located in a technical room within the building.

2
LEED Fellow
7group / Energy Opportunities
LEEDuser Expert
4461 thumbs up
Thu Jul 2, 2015, 2:57 pm

Take credit for variable temperature setpoints in hotel rooms

NC-2009 EAp2:Minimum energy performance
posted by  Sandra Holmström  on 

We have a hotel project where heating setpoints in hotel guest rooms are 21 degrees Celsius when the room is occupied and lowered to 18 degrees Celsius when the guests are not in the room.

3
LEED Fellow
7group / Energy Opportunities
LEEDuser Expert
4461 thumbs up
Thu Jun 18, 2015, 12:36 pm