Forum quick links
CO2 monitor in a booth
CI-2009 IEQc1:Outdoor Air Delivery Monitoringposted by Alicja Bieszyńska on
Hello!
100% OA VAVs
CI-2009 IEQc1:Outdoor Air Delivery Monitoringposted by Jeremy Kuhre on
We are remodeling two floors of a high-rise office tower. A 100% OA VAV introduces OA into the mechanical room for each floor where it is mixed with return air.
CO2 Monitors in Waiting Room Without 4 Walls
CI-2009 IEQc1:Outdoor Air Delivery Monitoringposted by Michelle Halle Stern on
I'm working on a HC interiors project with waiting rooms and nurse stations that have density of 25 people/1000sf, however they do not have 4 walls enclosing the spaces.
Automated control
CI-2009 IEQc1:Outdoor Air Delivery Monitoringposted by Max Calabro on
I notice the credit language here requires an alarm when CO2 levels are more than 10% above desired.
Too many densely occupied spaces
CI-2009 IEQc1:Outdoor Air Delivery Monitoringposted by Rubén M. R. on
Hello everyone, I am working on a three-level commercial office project.
Alternative to OA airflow measurement device at Building AHU
CI-2009 IEQc1:Outdoor Air Delivery Monitoringposted by Kristopher Baker on
So like many on this thread, i have a LEED CI project that is 1/3 of 1 floor and is served by the base building AHU that is outside the scope and LEED boundary of the project.
Locker rooms
CI-2009 IEQc1:Outdoor Air Delivery Monitoringposted by Agnieszka Rylska on
Are CO2 sensors required in locker rooms? Loker rooms are non-regularly occupied spaces but they are also densely-occupied spaces.
Outdoor Air Delivery Monitoring System for LEED CS building
CI-2009 IEQc1:Outdoor Air Delivery Monitoringposted by Ron Dean on
We have a leased office in a LEED C&S project.
Other routes for airflow measurment devices
CI-2009 IEQc1:Outdoor Air Delivery Monitoringposted by Mike D on
Are there any other ways of achieving the credit for non-densely occupied spaces using another route than airflow measurement devices ?