If you have non-densely occupied spaces served by an existing AHU, how should the outdoor airflow measurement be handled? There is no baseline for when an alarm should occur on the ventilation air since not all spaces are within the LEED scope and no minimum ventilation rate has been calculated via 62.1. On our specific project, there are 10 floors served by multiple 100% outside air units. We are doing work on a very small portion of multiple floors. The units are not within our scope of work. Short of adding an alarm to each valve providing airflow to each renovated space, which would get very costly very quickly, what would qualify for this credit? We have no problem meeting the CO2 sensor portion of this credit.

4

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Thu, 09/22/2011 - 15:20

What you have going for you is that the units are providing 100% outside air. That is much easier to monitor than minimum OSA fans. However, you would likely need an airflow station and alarm (or control wiring to a BMS) at each OSA entrance in order to satisfy the credit.