Hi, I am modeling an existing school building which is undergoing substantial renovation. As a part of the renovations, new windows are being added and the grade level is being changed. Per Appendix G, it seems like the window area for the baseline will need to the total prior to the renovation changes (in this case, baseline area will be lower than proposed). Is this interpretation correct? Also, should the grade levels be different as well? This means exposed wall area will be different between baseline and proposed building. There will be more below grade walls in the baseline as compared to the proposed case. Thanks in advance.

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Tue, 05/16/2017 - 15:03

I think the area of fenestration and above grade wall must be the same in both models. I don't think your interpretations are correct. Table G3.1-5 Baseline requires that these areas are identical between the Baseline and Proposed. Table G3.1-5 Baseline (f) is not an exception to this overall requirement. The existing conditions referenced would be the performance parameters (U-values, etc.) associated with the existing windows/walls, not the area. The area is already clearly addressed at the top of this column.