EBOM-2009 EAp1:Energy efficiency best management practices - planning, documentation and opportunity assessment

Sequence of Operations

Hello LEEDuser forum, I am doing the documentation for a small building (4,500 sq. ft) with a small mechanical system. I have made my way through the documentation requirements for EAp1, but the Sequence of Operations has me stumped. All the examples I have found are for much larger systems than the one I am working with. Any suggestions?

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Sat, 02/01/2014 - 02:31

Hi Martha, for smaller / less complex mechanical systems the sequence of operations is typically quite simple. For example: OCCUPIED Outside air damper opens, supply fan energizes, heating/cooling cycles to maintain space temperature. UNOCCUPIED Supply fan is off, outside air is closed, heating cycles to maintain space setback temperature. Hope this helps.