NC-2009 IEQc6.2:Controllability of Systems—Thermal Comfort

Residential Building

Hi, We are working on a condo project where the residential units have a space called "Living Area". This "Living Area" includes living room, dining room & kitchen, with one shared thermal control. The reviewer's comment is "It appears that not all shared multi-occupant spaces have been included in the form (such as kitchens in the residential units). Please provide a revised form to confirm that all shared multi-occupant spaces have been included in the form." We already put "living room" in the form. Can we just add "kitchen" to the form with the same "# of Spaces with Controls" as the "living room"? Or do the kitchens need separate thermal controls? Please advise. Thank you.

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Wed, 03/20/2013 - 23:23

That sounds a little convoluted—I would try emailing your reviewer to clarify, including a note in your narrative, and/or relabeling the entry on the form as Living/Kitchen/Dining.

Sat, 03/23/2013 - 00:38

Per the IEQ Space Matrix, you need to only have one thermal control per residential unit to meet the requirements. That comes from cell U6 of the BD+C tab of the July 2012 version of the IEQ SpaceMatrix.