Reviewer comment asks us to provide "The effect on occupant service capabilities" of the capital measures identified during the level II audit.
I want to know what is the definition of "occupant service capabilities"?
Thank you.
Forum discussion
EBOM-2009 EAc2.1: Existing Building Commissioning—Investigation and Analysis
Hi,
Reviewer comment asks us to provide "The effect on occupant service capabilities" of the capital measures identified during the level II audit.
I want to know what is the definition of "occupant service capabilities"?
Thank you.
LEEDuser is supported by our premium members, not by advertisers.
Go premium forTo post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.
Tristan Roberts
RepresentativeVermont House of Representatives
LEEDuser Expert
11478 thumbs up
November 4, 2013 - 9:39 pm
Magda, I don't know—never heard that term before. Can you provide a more complete quote?I would ask GBCI to clarify the reviewer comment.
Dave Hubka
Practice Leader - SustainabilityEUA
LEEDuser Expert
530 thumbs up
January 22, 2014 - 9:05 am
"occupant service capabilities" is language from the referenced standard. It is asking how the implemented measure affects the occupant's ability to control/adjust their setpoints/operating hours/etc.
Many times the practical capital improvement meausures we identify has no effect on ocupant service capabilities; therefore we note in our report 'not applicable to this capital improvement measure".