FAQs about EAp2 :

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

View answers »

Forum discussion

NC-2009 EAp2:Minimum energy performance

Modeling 100% Fresh Air Casino Floor in LEED v4.1

I am working on a hotel project where the ground floor is entirely dedicated to a casino. This casino floor is served by 8 AHUs, all supplying 100% fresh air. These AHUs are equipped with heating and cooling capabilities to meet the space loads, and they include heat recovery wheels.

Is there a specific way to model such spaces according to LEED v4.1? If I model them using the usual approach (assigning System 7 or 8), the project appears less efficient than the baseline because the entire floor is supplied with 100% fresh air. Any guidance on how to address this in the energy model would be greatly appreciated.

Thanks in advance.

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Thu, 02/20/2025 - 14:48

It is not at all unusual for the comparison of air to water systems to show a negative savings. If the code requirement for OA is less than the proposed design you pay a penalty for that design decision as well. So I am not surprised. Did you look through the G3.1.1 exceptions? Any apply?

Thu, 02/20/2025 - 18:21

Thank you, Marcus, for the quick reply. I reviewed the G3.1.1 exceptions, but unfortunately, none of them apply to my project.