Liquid Ice Melt

Can anyone provide guidance on the types of Liquid Ice Melt that would satisfy the requirements of this credit?

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Fri, 11/23/2012 - 16:12

Cathy, there is some good guidance on this in the Checklists tab above on LEEDuser. Please post back with any more specific questions.

Tue, 04/29/2014 - 17:05

We received a review comment that the amount of sodium or calcium chloride in the deicer product must be less than 5%. Is there a place where this is specifically mentioned as the requirement? Thank you

Tue, 04/29/2014 - 17:32

Hi Cathy, LEED Interpretation 10146 (from April 2012) states that "deicer products that contain no greater than 5% of Sodium Chloride (NaCl) or Calcium Chloride (CaCl) in their applied state" are compliant. I believe this is the only place this rule is mentioned.