Forum discussion

CI-2009 EAc3:Measurement and Verification

LEED project defined boundary 1.5 buildings

Just to be sure, to be sure, not trying to be picky here. Our new LEED-CI project encompasses 2 buildings, but only 1 is going to be fully occupied and the other only partially,

3

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Mon, 06/27/2011 - 16:31

To be consistent with the intent of the credit, it sounds like you'd want to follow Case 2 (prepare an M&V plan) for the full occupied building and follow Case 1 (sub-metering) for the partially occupied building.

Thu, 06/30/2011 - 10:34

Yes sir, but not sure if a hybrid is permitted. However our MEP argued from a holistic perspective, the M&V plan is unnecessary (work) so our approach should be to follow Case 1, arguing that the total space constitute <75 percent of total area thereby we simply submeter. What you think? A quick reply is appreciated, I got to conclude this matter in a meeting tomorrow!

Mon, 11/21/2011 - 20:55

The first question that I would pose is whether these two buildings/projects can even be submitted as a single CI project..... I would think not.

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.