Hello, We have a project where the CS and one CI tenant is being built at the same time. Do any of the Exemplary Performance credits carry over such as Alt transportation, light pollution, open space or water use reduction if the bathrooms are dedicated to the tenant but built as part of the CS? Thanks

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Wed, 05/21/2014 - 14:59

Transportation and Water Use Reduction are individual CI credits so you should be able to achieve the EP points for them in both rating systems. To get the WEc1 points in CI you need to include the consumption in the base building fixtures the tenant is using, regardless of when they were constructed. Light Pollution is an SSc1 credit which is not eligible for the EP under path 12, so you won't be able to use that.

Wed, 05/21/2014 - 15:07

Thank you, that makes sense. I will have my engineers look into it.