Our store is located in a shopping mall where customers have no access to WCs in the shop, but use the WCs provided within the main shopping mall. Do we need to include these shared WCs for the LEED assessment when calculating transient water use?
You rely on LEEDuser. Can we rely on you?
LEEDuser is supported by our premium members, not by advertisers.
Go premium for
Tristan Roberts
RepresentativeVermont House of Representatives
LEEDuser Expert
11478 thumbs up
July 31, 2013 - 12:30 pm
Blythe, you would not need to do this, no.
María Fernanda Aguirre
Architect LEED AP BD + C - LEED AP ID + CRenato Miranda and Associates
7 thumbs up
July 31, 2013 - 12:48 pm
Blythe: When you certify a project under CI (or CI Retail) rating System, one of the principles is to select wisely the building where the project is located. In fact for prerrequisite WE p1, in the Leedonline template you must select between 4 options, and you can choose to exclude fixtures outside the tenant space (last option) . That means, it is not neccessary to include them but you have to be careful if you are pursuing Credit SS c1, through option 2, path 10 because in that case both options are not compatible.