For a building pre-occupancy flush-out what are the requirements for substantiating that the 14,000 cfm of OA was actually completed for the entire square footage. In the past under version 2 the only way that was acceptable to reviewers was showing a trend graph from the controls automation system which requires a flow sensor installed in all air handlers to be read in the automation software. Is this not the case any longer?
You rely on LEEDuser. Can we rely on you?
LEEDuser is supported by our premium members, not by advertisers.
Go premium for
Tristan Roberts
RepresentativeVermont House of Representatives
LEEDuser Expert
11474 thumbs up
July 26, 2014 - 8:37 am
David, there is no specific documentation requirement such as the graph output you mention. A narrative is what the LEED Online form asks for.