Hi, It is a general practice to use Fevicol SR 998 as duct insulation adhesive due to its bonding with the ducting material. However the VOC content of this product is 700 grams per litre. I am not sure which application is best suitable and the VOC limit which needs to be followed. I am facing this problem for all my projects. Will this fall under sheet applied rubber lining operation ?

1

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Fri, 02/08/2013 - 10:57

From USGBC Interpretations: "Project teams may classify duct sealants under "Other", as listed in the SCAQMD VOC Limits table. Applicable Internationally." The maximum allowable VOC content is 420 g/l. We have found a number of very low VOC duct sealants which meet this criteria and are of high quality.