If the project schedule indicates that move in will occur prior to the completion of furniture installation, can this credit be achieved by flush out?
You rely on LEEDuser. Can we rely on you?
LEEDuser is supported by our premium members, not by advertisers.
Go premium for
Tristan Roberts
RepresentativeVermont House of Representatives
LEEDuser Expert
11478 thumbs up
August 26, 2017 - 2:51 pm
Michelle, the credit language seems quite specific that flushout must occur after furniture installation.
Summer Minchew
Managing PartnerEcoimpact Consulting
LEEDuser Expert
173 thumbs up
December 20, 2017 - 3:06 pm
Tristan, agree that the language is specific that flushout must occur after furniture installation but what about furniture that is reused (i.e. is over 1 year old and is being relocated with the tenant occupants)?
Tristan Roberts
RepresentativeVermont House of Representatives
LEEDuser Expert
11478 thumbs up
December 21, 2017 - 3:19 pm
This has sometimes been a gray area in LEED—there have always been specific requirements that don't really make sense to apply to existing materials/furniture, but do.... or it least it appears that they do, but do they really?
In this case, I don't see anything in the credit language or a LEED Interpretation that would allow for an exception. I think you'd have to submit a CIR, or at least ask GBCI.
emily reese moody
Sustainability Director, Certifications & ComplianceJacobs
LEEDuser Expert
487 thumbs up
December 21, 2017 - 3:32 pm
Summer, is this a case where you could do the Option 1 Path 2 approach? Does the furniture timeline fit within that timeframe?
I agree with Tristan; I would email LEEDCoach and ask about the existing furniture. Hopefully they'd be logical and approach it like they do for the Energy Star equipment, where the requirements only apply to items 1yr old or newer at the time of move-in (which is also not explicitly stated in v4 like it was in v3...I had to email to be certain).
Summer Minchew
Managing PartnerEcoimpact Consulting
LEEDuser Expert
173 thumbs up
January 4, 2018 - 12:01 pm
Thanks Emily and Tristan. Our LEED Coach was unable to review credit strategies for compliance outside of the formal review process so we have submitted a CIR.
Summer Minchew
Managing PartnerEcoimpact Consulting
LEEDuser Expert
173 thumbs up
January 30, 2018 - 10:12 am
Following up - our project specific ruling came back as follows: "The project is requesting that existing furniture (more than two years old) from an alternate location be exempt from the requirement in LEED ID+C v4 EQc Indoor Air Quality Assessment that all furnishings be installed before the preconstruction flush-out or testing, for this project. Yes, this is acceptable."
Tristan Roberts
RepresentativeVermont House of Representatives
LEEDuser Expert
11478 thumbs up
January 30, 2018 - 7:34 pm
Great feedback, thanks for sharing!