There are different departments with each having multiple shifts, each of the shifts having different start time & end time. (For example, department A has 3 shifts with 1st shift time of 6 am - 3 pm, 2nd shift time of 10am - 8 pm, 3rd shift time of 2 pm - 11pm. Similarly, department B has 2 shifts with 1st shift time of 8 am - 4pm, 2nd shift time of 1 pm - 9 pm & assuming an occupancy of 50 people in each shift & about 50 visitors overall). How to calculate FTE for this kind of occupancy? What number is to be considered for the showers, bicycle racks & water use calculations? In actual we have about 7 departments & each one has varying number of shifts, times & occupancy. I also tried putting the occupancy numbers in a 24 hour cycle to check the overlap of the occupant & it turned out that the maximum number of occupants (200) are in the premises only for about 1 hour. So if I calculate FTE based on this maximum number, it turns out to be very low (200 X 1/8 = 25). Also please note that none of the occupants share the desks.
You rely on LEEDuser. Can we rely on you?
LEEDuser is supported by our premium members, not by advertisers.
Go premium for $... »
Tristan Roberts
RepresentativeVermont House of Representatives
LEEDuser Expert
11478 thumbs up
January 10, 2011 - 7:10 pm
I think I would take the same approach you did and look at it on a 24-hour cycle, and look for overlaps and maximums. I think you have the right approach.