You rely on LEEDuser. Can we rely on you?
LEEDuser is supported by our premium members, not by advertisers.
Go premium forForum discussion
Schools-2009 IEQc9: Enhanced Acoustical Performance
LEEDuser is supported by our premium members, not by advertisers.
Go premium forTo post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.
Daniel Hicks
Daniel Hicks, E.I., INCEGeiler & Associates
267 thumbs up
September 24, 2014 - 5:23 pm
You could do a "composite STC calculation" to try to determine if they have any effect on the overall STC rating of your wall or floor/ceiling. But I'm going to bet that the square footage of expansion joint compared to the square footage of the wall assembly is so small that it's probably not very significant.
The process for a composite STC calculation is outlined in the ANSI standard if you're interested.
I don't believe you'll need an NRC rating for the expansion joint, unless I'm not understanding your question. You'll only need NRC ratings for the items that provide acoustic absorption in the space.