FAQs about EAp2 :

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

View answers »

Forum discussion

NC-2009 EAp2:Minimum Energy Performance

Energy Modeling using “HAP”

I am doing the energy model for a project. The project total area is “153,145 sf”, 25,346 sf area of the total area is condition and the other “127,799” sf area is unconditioned, “ventilation fan and louvers” are using for unconditioned area. Please comments on it. 1. How can I model the ventilation system in Baseline and in Proposed model? 2. HVAC Baseline system depend on only condition area or the total area of project?

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Fri, 05/27/2016 - 17:38

1. This is modeled identically as a process load in both models. Since it does not affect the loads it is just a motor running for a certain period of time so schedule it according to how the fans are expected to run in the project when operational. 2. Conditioned area.

Tue, 05/31/2016 - 07:23

Hi Marcus, Thank you for your comments. i modeled the ventilation fan as a process load in both model. project offices area conditioned by "VRF system", and offices area modeled as per design documents and baseline as per "Table G3.1.1A" . please clarify some more issues regarding unconditioned spaces. 1. when i modeled the unconditioned spaces with VRF system, then “unmet load hours” increased by more than 300. 2. Can I use any HVAC system type except “VRF system” identically in baseline and proposed model for unconditioned spaces? 3. If I use any HVAC system type in project unconditioned spaces, then how can I model the Baseline HVAC system,its model as per "Table G3.1.1A "or identically model same specification in both energy model.

Tue, 05/31/2016 - 13:55

Unconditioned spaces do not have any heating or cooling equipment installed so they have no loads to meet. 1. You should not model the VRF system in unconditioned spaces. 2. You should only model any fans in the unconditioned spaces identically. You should not have any heating or cooling system in an unconditioned space. 3. You don't model any HVAC system type in an unconditioned space.

Wed, 06/01/2016 - 11:38

Thanks Marcus, My project is denim factory.It process load is 945 kw. This process load is Denim coating and BENNINGER machines.if i model this process load in unconditioned "Hall" the energy saving is reduce. 1 How to model the process load ? Can i simulate the models with reduce process load? 2 If i use the "Exponential Calculation" which standard i follow for "VFD" based Denim machines. ? "VFD machines are energy efficient.

Wed, 06/01/2016 - 12:52

1. How you model a process load depends on the software you use. Since it is located in an unconditioned space you could possibly perform the calculations outside the modeling software assuming it will not impact other energy use. 2. To show savings for a process load you must follow the exceptional calculation method. You must develop your own baseline for comparison and provide justification that you have selected a reasonable baseline. The baseline should be based on standard industry practice in your location. So in this case if installing constant speed equipment is the norm then that can be the baseline. However you will need to provide some evidence that is the case you can't just say constant speed is the norm. Establishing a reasonable baseline is often the hardest part of an exceptional calculation so I urge you to be thorough in your justification.

Thu, 06/02/2016 - 06:36

1. I am using "HAP" software. Model the process load in "Electrical Equipment" tab. 2. Unfortunately in our region still no establish any industry code for process load. 3. Can i follow the NEC standards or any other? 4. When i use the "Exceptional Calculation" for process load, then process load shall model in space or only separate calculation.

Thu, 06/02/2016 - 15:17

1. Ok I suppose. 2. There are really no industry codes for process loads anywhere in the world. 3. Not sure. 4. Whether you model it in the space or separately will depend on if it interacts with other loads in the space. If the space is unconditioned and there are not any heating, cooling, ventilation, etc. loads that are impacted then it does not have to be modeled in the space.

Tue, 03/12/2024 - 09:07

Hi Marcus Can we model process load in HAP v6? It has an Option to model to acumulative load in SYSTEMS

Tue, 03/26/2024 - 23:46

We see process loads included in HAP models all the time so yes you can. Eactly how you do that is a better question for HAP technical support.