My client has access to the following program:
Pre-purchase a 20 year commitment to a 100% renewable, local energy product from the local power provider (EverGreen from Sonoma Clean Power). The cost of the pre-purchase will be determined by the annual electricity usage in Kwh from the T24 2013 energy code documentation multiplied by the cost premium of the power provider’s 100% local, renewable product over the power provider’s standard product. The pre-payment would be paid into an account for building additional local renewable sources. Once built, the occupant of the commercial space would pay the default product rate for energy while receiving the 100% local, renewable product for twenty years. The benefit would remain with the tenant space or property if it is sold, just like a solar array.
I believe the local utility, community choice aggregator CCA, has also petitioned the State of California to allow the use of this program in place of the State required onsite solar PV as well.
Do you think that we use this program in place of an onsite solar PV array?
Thanks!
Kevin
Marcus Sheffer
LEED Fellow7group / Energy Opportunities
LEEDuser Expert
5597 thumbs up
August 22, 2018 - 1:55 pm
It would need to meet the LEED criteria for off-site renewable energy systems which include - a 10 year or more contract, same utility service territory, and all RECs must be retained or replaced.
Kevin Gilleran
presidentGilleran Energy Management, Inc.
18 thumbs up
August 22, 2018 - 2:48 pm
Marcus,
As a follow up question:
Assuming that I clarify with the utility that 100% of the provided power is renewable and RECs are also available can we take credit under both EAc2 Energy Performance , EAc4 Renewable Energy Production and EAc6 Green Power and Carbon Offsets for the same Evergreen power.
I will check to verify that the RECs are Green-e Energy certified or equivalent.
Thanks again for your timely support!
Kevin
Marcus Sheffer
LEED Fellow7group / Energy Opportunities
LEEDuser Expert
5597 thumbs up
August 23, 2018 - 11:33 am
If it counts for EAc4 then it will count toward EAc2. It might also count for EAc6 but that gets a little murky when you are net zero. Check the Reference Guide on that one.
Iqbal K.
DirectorGeo Rumbia
November 26, 2020 - 8:17 am
Dear Marcus,
Any solution when the REC for local territory is not available, and we have limitation on-site to provide RE. Is it possible to buy accross the regional province, maybe country. For example the project is in Asia and the REC from US?
Thanks for your support.
Best regards,
Iqbal
Marcus Sheffer
LEED Fellow7group / Energy Opportunities
LEEDuser Expert
5597 thumbs up
November 27, 2020 - 12:48 pm
Yes I believe that you can buy US based RECs for projects anywhere in the world.