Forum discussion

EBOM-2009 IEQc1.2:Indoor air quality best management practices - outdoor air delivery monitoring

Densely occupied spaces exemption

Hi All, We have a project that has a lot of meeting rooms (area of each room is smaller than 150 square feet) that can accomodate 4 person per meeting room - therefore considered densely occupied and should be provided with CO2 sensors. However, the reference guide states that individual rooms smaller than 150 square feet are exempted. Which will govern?

1

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Tue, 10/16/2012 - 13:14

Hi Mary Ann The exemption for rooms smaller than 150 square feet would be the overriding factor. Thanks, Hannah

Fri, 10/19/2012 - 19:44

It'd be nice if GBCI would apply this minimum to all project types not just EBOM. There are a number of credits across all the project types where a minimum SQFT would help take into account a reasonable ROI. Maybe in v4!

Fri, 10/19/2012 - 19:58

Hi Dylan Did you see the 5th public comment for LEED v4 is open? I'd strongly recommend adding your comments here if you haven't already: https://new.usgbc.org/

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.