CS-2009 IEQc4.3:Low-emitting materials - flooring systems

Carpark surfaces

Hi everybody. I have a problem in the project which i am leading the LEED certification. We have parking areas inside of the building basement floor. While i am prepearing the space usage table, parking areas are excluded from total gross floor area. Should we follow the ieqc4.3 VOC requirements in parking areas that inside of the building? Or, are these areas are excluded for this credit?

Thanks in advance

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Thu, 12/21/2017 - 18:50

Ekin, IEQc4.3 requirements don't just apply to gross floor area. They apply to area within the building's weather barrier, so they would apply to the parking spaces.

Fri, 12/22/2017 - 05:33

Hi Tristan, Thank yo so much. We should follow the flooring systems on the parking floors.

Fri, 12/22/2017 - 05:40

Also, should we follow IEQc3 on the parking floors?