NC-2009 IEQc6.2:Controllability of systems - thermal comfort

Bus Bay Areas

Should Bus Maintenance Bays be included in this credit? People work in this areas more than 8 hours a day but how would you show compliance? No task lighting and only onw switch for the whole warehouse. Thanks

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Fri, 01/18/2013 - 21:26

Victor, it seems like these spaces shoud be included in the credit as multi-occupant spaces. 

Sun, 01/20/2013 - 18:25

Hi Victor, I do think you need to include these spaces for credit compliance. However, I disagree with Tristan (sorry about that Tristan). The intent of the credit is to give occupants greater control of their thermal comfort. The occupants in this space are in various areas doing different tasks. This is not the case in "multi-occupant" like conference rooms where everyone is in the same often densely occupied area doing essentially the same thing (same level of activity). So, to meet the credit requirement for the space in question I think you would need to provide spot conditioning (e.g., spot coolers and radiant heaters) for 50% of the occupants. Doing so, would meet the credit intent and the requirements.