FAQs about EAp2 :

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

View answers »

Forum discussion

NC-2009 EAp2:Minimum energy performance

ASHRAE Mandatory Provisions & Existing skylights not replaced

Hi everyone, I'm currently working on a major renovation project. The owner is renovating & insulating the entire building but doesn't wish to replace the existing old single glazing skylights for budget reasons. Obviously, the existing skylights don't meet the ASHRAE Mandatory provisions. The question is, are the skylights excluded from the need to meet the mandatory provisions since they are not part of the scope of work on this renovation? Or does the ASHRAE mandatory provisions are forcing us to replace those skylights in order to be certified? Thank you in advance, Regards,

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Wed, 06/11/2014 - 14:10

Window and skylight performance are not mandatory provisions so no worries there. You are not required to replace them. In the energy models they are included identically.

Wed, 06/11/2014 - 15:15

Has your energy modeler simulated the energy savings that could result if you replace the skylights? This kind of cost/benefit analysis could change your Owner’s mind.

Thu, 06/12/2014 - 04:56

Thank you Marcus, the roof and wall minimum insulation though are mandatory provisions, right? Jon, the energy model is being done now and we hope to have some cost analysis to present to the owner before any decision is taken, but we are working on a very tight schedule for this project...

Thu, 06/12/2014 - 12:59

Nope. All of the requirements in the 5.5-X tables are prescriptive and not mandatory.