Forum discussion

EBOM-2009 IEQc1.2:Indoor air quality best management practices - outdoor air delivery monitoring

Airflow measuring devices on MUA

I am working on a office building that has installed airflow measuring devices on the central Makeup Air Unit which serve fresh air to a compartment unit on each of the buildings floors via a fresh air damper (8 floors). No floors have densely occupied spaces. Would I be able to achieve the credit without airflow measuring devices on each of the compartment units? Thanks.

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Tue, 12/01/2015 - 16:56

The airflow measuring devices have to be located at the system level. So, if the MAU is serving separate AHUs on each floor, a single measuring device located at the MAU would not be sufficient. You would need one installed at each AHU.

Fri, 06/03/2016 - 16:20

Ben, where in the credit would I find the actual text that states this? I am in the same situation.

Mon, 06/06/2016 - 15:16

Hi David, this requirement is included in the rating system language. See Case 1 - 2nd paragraph - first sentence on page 361 of the reference guide.

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.