Dear Sir/ Madam,

I have a project that is a hotel with 200 guest rooms that are non-densely occupied. Each guest room floor (20 rooms per floor) is supplied with 3 AHUs. Therefore 100% of the OA suppled by these AHU are served in to the non-densely occupied spaces. However if I calculate based on the total OA requirement of the building there is no single guest room that takes 20% or more OA from that total OA requirement, but add up 200 guest rooms and then altogether they take more than 20% OA.

Based on that I have the following questions.

IEQc1 requires direct air flow measurement devices mechanical ventilation systems where 20% or more of the design supply airflow serves non-densely occupied spaces. But I'm not sure whether I should define "space" as a single guest room unit or all guest rooms together (because one AHU supplies air to multiple guest rooms).

Secondly I'm also not sure whether 20% OA requirement is based on the total OA requirement of the building or the outdoor air supplied by each AHU.

I appreciate clarification on this.

Thank you very much.