NC-v4 EQp1:Minimum indoor air quality performance

Zone Secondary Recirculation Fraction

ASHRAE 62.1, Section A1.2.2 states:

Er is less than 1.0 for plenum return systems with secondary recirculation (e.g. fan-powered VAV with plenum return)

Er is 0 for ducted return systems with secondary recirculation (e.g. fan-powered VAV with ducted return)

Er is 1.0 for systems with system-level recirculation (e.g. dual-fan dual duct systems with ducted return)

Other system types = 0.75.

 

Our system is NOT dual-fan or dual-duct and our VAV boxes do NOT have fans and do NOT have secondary recirculation so I would assume this system would be defined as 'other types' and the Er would be 0.75.

GBCI review comment:

The Ventilation Rate Procedure (VRP) calculations have utilized a Zone Secondary Recirculation Fraction, Er, of 0.75. This value is typically used for fan-powered terminal units. Based on the mechanical schedules provided in PI Project Information, the terminal units are shut-off VAV boxes (non-fan-powered); therefore, the Er value should be zero or left blank.

So I guess Er is zero for non-fan powered boxes. But do not understand the logic.

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Thu, 05/08/2025 - 17:58

Hi Dave, I am having a lot of confusion regarding this Er value. I am not understanding what does it represent in practice. I wonder if you managed to solve your issue. I am working on a similar case with fan-powered VAV with plenum return, in this case it states that Er value <1, what does this exactly mean. Which number should i input in the calculator as Er? 0.99?0.1?0.5? based on what? Thanks