Forum discussion

NC-2009 IEQp1:Minimum indoor air quality performance

Zone air distribution ventilation effectiveness

I need help with determining proper case for the Air Distribution Configuration per table per Table 6-2. The forth entry required a velocity of 150 cfm to be reached within 4.5 ft of floor levels. Does it mean that this velocity should be achieved at this height or this is the requirements for the velocity measured at grid level. Our mechanical engineer is claiming that this is velocity is too high for that height, and wants to make the case for 150 cfm to be measured at grid levels. Please advise!

1

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Wed, 04/18/2012 - 13:43

Maria, a terminal velocity of 150 fpm does need to be achieved at 4.5 ft above finished floor level. Ensure the supply air temperature is no greater than 15 degrees above the room setpoint, to limit the potential for stratification in heating mode. It's a good idea to use an Ez of 0.8 for heating design, regardless.

Wed, 04/18/2012 - 13:40

Roger, you are correct in saying that the velocity must be 150 fpm at 4.5 ft AFF. However, simply having a SAT of less than 15 degF higher than room setpoint is not an alternative that will allow you to use an Ez of 1.0. To use Ez 1.0 you must comply with both the temperature and the air jet requirement. In my experience it is almost impossible (because of the velocity requirement) to use an Ez of 1.0 with a ceiling supply and ceiling return system for both heating and cooling.

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.