Forum discussion

NC-2009 SSc7.2:Heat island effect - roof

Would permanent and attached seating count in roof calculations?

I have a roof of a building which has a light colored concrete surface and should in theory meet the requirements of the credit. The majority of the roof area though, is covered with permanent & attached seating (although when the building is not in use, the seats are tilted upward). Any experience on whether seating counts towards appurtenances and can thus be excluded?

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Wed, 04/11/2012 - 13:28

Based on this reference guide addendum definition, I'd assume that seating can be excluded: "An appurtenance is any built-in, nonstructural portion of a roof system, such as skylights, ventilators, mechanical equipment, partitions, and solar energy panels." It may be helpful to submit a project-specific CIR, as I didn't find any LEED Interpretations addressing this issue.

Wed, 04/11/2012 - 20:10

Thanks Samantha! One follow-up question, do we think I should exclude the entire seating area, or just treat it as though it doesn't exist and include the underlying concrete surface?

Thu, 04/12/2012 - 13:15

You're welcome. LEED Interpretation 5676 addresses a similar situation. It states that mechanical equipment covering 30% of the roof can be excluded from the credit calculation, but to reduce heat island effect the project team should consider installing light-colored mechanical equipment. Based on this I'd say you can exclude the roof area covered by the seating in the calculation (and consider using light-colored seating), although if the roof below the seating is SRI compliant it wouldn't matter if you excluded it or not. This LI has not yet been approved or considered for 2009 projects, so the reviewer may consider it appropriate for your project if you were to reference it in your submittal.