FAQs about EAp2 :

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

View answers »

Forum discussion

NC-2009 EAp2:Minimum energy performance

Window Assembly - LBNL vs European Software

Dear all, Our project recently received the comment below regarding window assembly U-value calculations. The project is located in Ireland and therefore the assembly values (which include frame and glass) have been calculated via a European software which complies with BS (British Standard), EN (European Standard) and ISO requirements. The following comment specifically refers to the LBNL software, however is it acceptable to demonstrate compliance with an European alternative? Provide additional information to confirm that the framed assembly U-value was used for the Proposed Case windows (such as: showing that the whole window assembly has been tested by NFRC; verifying that LBNL Window5 calculations have been provided for the whole assembly; or verifying that the frame effects are captured within the energy modeling software).

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Tue, 08/09/2016 - 09:31

Hi Martin, The reviewer seems to be giving you 3 options to comply here. As you correctly allude to - 1. NRFC tests are not likely to be carried out for EU Fenestration assemblies. 2. You could use WINDOW5 and calculate the entire U-value and show the reviewer these calculations and/or 3. Show the reviewer inputs to your simulation software that the entire U-value (including frame) has been used. Option 3 seems like the best bet as you seem to have calculated via this method. Regards Graham

Tue, 08/09/2016 - 10:51

I agree with Graham. Moreover, you could upload a datasheet relative to the windows and show to reviewers that the model is coherent with the real data. Pay attention: the surface resistance coefficients of the European standards are different from the coefficients of the ASHRAE standard, which are considered for the U-values of the baseline case, if the building is a new construction.

Tue, 08/09/2016 - 13:28

I agree. Tell the reviewer what you based the assembly U-value on, how you have modeled it and provide the documentation you mention above. All too often modelers do not get this right when trying to model the frames separate from the glass. That will frequently produce results that are too low.