We have a new hospital building pursuing LEED-HC that is currently under construction. The hospital just announced a lease with a separate owner that plans on building out a full floor of inpatient / operating suites. This build-out will be 7% of the entire hospital area (the remaining 93% is owner-occupied), will be leased by another entity, will be built by a separate contractor, will be completed at the same time as the main hospital building and does not plan on pursuing LEED-CI. The build-out will make alterations to the building envelope at that floor and may make potential changes to the HVAC system on that floor. We were just prepared to submit design credits for review for the overall project, but our MEP engineer has raised concerns about the energy model. Does this new separate build-out project mean that we must modify the energy model of the overall project to take any envelope and HVAC changes into account? Thanks.
Well, that is an unfortunate situation. Who decides to build a LEED HC building and then lets a portion of it completely slide away from that standard, especially for critical patient care areas like surgery?
There are a couple of things going on here beyond the energy model question but let's tackle that one first. My reaction is yes because the envelope is changing and the HVAC is likely to change. Given the tenant use, HVAC change is likely. This will impact the performance of the building. You may want to go ahead and submit your project for review and include a narrative about this situation and ask for advice from the GBCI. You could also call and request a consultation on this issue. They will want you to know for certain what the other team is planning on doing with the mechanical and envelope systems.
The other issue I see is going to separate the LEED spaces from the non LEED space. The GBCI will require you to accurately sign the project such that the non LEED space is not assumed to be LEED certified. Think 'you are entering a LEED building' at all connections to this tenant space.
A tricky condition will be the tenant space as shell space. Whenever I submit a project with shell spaces which is often, the GBCI wants policies and signed letters stating that these shelled spaces will be fitted out to the LEED standard of the building. What I'm not sure about is how you can convince them that this 7% is tenant and not essentially shell space. How are you dealing with the site credits? You now have to sign the LEFEV parking to the LEED building only and exclude the surgical patients (for example, I don't know you're doing that credit). I recommend you read the campus guides. The forum is here: http://www.leeduser.com/topic/new-leed-guidance-campuses-and-multiple-buildings?__ETA: Okay, that link didn't work out so well. If you go to the Forum tab, there is a Hot Topic in LEED area to the right and you want the Multiple Building forum listed there. Here's the newest Campus Guidance which I think you need to read to see if or how it applies. http://www.usgbc.org/resources/campus-guidance