FAQs about EAp2 :

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

View answers »

Forum discussion

NC-2009 EAp2:Minimum energy performance

Which system

I have a project I am trying to model. the overall building is just over 25,000sf. The is an office area that is about 11,000sf and enclosed parking area, and an enclosed utility space. The office area is conditioned by a heat pumps system. the enclosed parking and other spaces are heat only with radaint heaters or hw unit heaters depending on the space. The enclosed parking also has a ventilation system. We originally submitted the building modeling it against a baseline system #4 Packaged heat pumps. the reviewer came back and said that since the building was over 25,000sf that we should be using system #5 Packaged VAV with reheat as baseline. So we re-modeled the building using system #5 as a baseline with a couple exceptions. Appendix G says that if you are using system #5 there is an exception to use a system #3 or 4 for areas that differ significantly from the rest of the building. We used that excepttion for the garage area and utility spaces. The reviewers still did not like that and came back and said that we need to model the garage and other utility spaces as semi heated. Looking at appendix G I do not see where it says we can model as a semi heated space. Appendix G also states that where attirbutes make the building eligible for more than one system that the most predominant system shall apply. Any one have any thoughts on what system I should be modleing as baseline? Where in appendix G does it talk about semi heated spaces?

4

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Wed, 07/06/2011 - 21:22

Check the heating capacity per square foot for the parking garage. ASHRAE defines a conditioned as being heated if it has a heating capacity that exceeds a defined value. There is a table in the definition section of 90.1 that lists the criteria for "conditioned - heated" for every climate zone (ASHRAE 90.1-2007 page 13). Below the conditioned space definition is also the semi-heated definition. If your space is considered "conditioned" follow the guidelines of Appendix G table G3.1 number 10 (hVAC Systems).