FAQs about EAp2 :

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

View answers »

Forum discussion

NC-2009 EAp2:Minimum Energy Performance

What will the minimum OA be if hood exhaust hood is present

We have a culinary school, the minimum OA per 62.1 is only 10k cfm, but the fume hood exhaust can go above 100k cfm. But 90.1 only says about modeling the same ventilation rate between proposed and baseline but didn't say about the fume hood exhaust. So should we also model the fume hood exhaust cfm identically between proposed and baseline? Also, for the fume hood fan energy, if I understand correctly, should be modeled identical per 90.1 6.5.3.1.1 exception c. Is this correct? Thanks in advance!

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Thu, 03/31/2016 - 13:37

The kitchen hood should be modeled identically as a process load. Section 6.5.3.1.1 applies to regulated fan power. Kitchen hoods are not regulated (that is why they are process and modeled identically). The fume hoods referenced in Exception c are the kind used in a lab. Kitchen hoods are not typically referred to as fume hoods.