EBOM-2009 WEc1:Water performance measurement

Weekly Reading Requirement for Option 1 AND Option 2?

Hi All, It looks like our team missed something and I want to be sure. We had always planned to pursue Option 1 (Whole Building metering), however, it seems like the weekly meter reading requirement comes into play for the whole building when Option 2 (submeter) is persued. Is this true? We just added irrigation meters and the weekly irrigation was read but not the whole building. Have we lost the whole credit (both Option 1 and 2), or can we still save Option 1, by dropping out of the submeter point (Option 2)? We are submitting soon, so starting whole building might not work at this point. To make it short: Are weekly readings always expected for Option 1 (whole building)? The Reference Guide really speaks to the weekly when the Option 2 guidance is explained, however, not as explicit in Option 1 guidance. Thanks, Michelle

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Sat, 03/23/2013 - 17:41

Hi Michelle Weekly readings are required for both options, regardless of if one or both are pursued. The readings need to be taken weekly over the performance period in order to qualify. Thanks