WBS: Exhaust Air Energy Recovery in Baseline HVAC

Hi! I have got a question regarding ASHRAE G3.1.2.10 "Exhaust Air Energy Recovery" which has to be applied to the baseline model. It says that at a minimum outdoor air supply of 70 % or greater of the design supply air quantity the baseline should be modeled with energy recovery. For this calculation do I use the outdoor air quantity over a whole year? Or can I take the m³/h-values derived from the sizing run and the minimum outdoor air rate?

1

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Mon, 07/23/2012 - 13:42

Sounds like it is based on the design supply air so that would be based on the peak loads at design conditions.