Hello, I am working on a large LEED CI project where the tenant is occupying the majority of an existing building. The restrooms in this building prior to construction had 3.5 gpf blow-out flush valve water closets. As part of the scope of work for this project the excising 3.5 gpf blow-out water closets are being removed and replaced with new tank type 1.4 gpf water closets to save water. Should the baseline case be the 3.5 gpf blow-out fixtures or does the baseline need to be a 1.6 gpf tank type water closet? Thank you, Brandon

2

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Thu, 05/26/2011 - 01:16

Brandon, the baseline is 1.6 gpf—per the credit language. It would be great to take credit for reductions from existing conditions but LEED doesn't allow for that!