VRF System Rc Value

we use VRF system for A/c we use value given in LEED guide Rc 2.2 lb/ton As per the the default calculation we get points but the reviewer tells Rc for VRF is very low it may be "3 - 6" lb/ton Is it possible to get points for VRF system

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Wed, 09/02/2015 - 11:32

awaiting For your Reply

Wed, 09/02/2015 - 20:48

The refrigerant charge (Rc) should be the actual amount of refrigerant being used. The table in the Reference Guide shows you the maximum charge that would still meet the credit - it is not a default. In the case of VRF (or any split system), you must include all the refrigerant in the distribution piping. This usually makes the credit very difficult for VRF systems to achieve.

Thu, 09/03/2015 - 07:12

Thank you for your support